1㎡左右排烟口测试平均风速

请问一下,部分地库设置的大尺寸的排烟口,我碰上过1㎡左右的,那么计算平均风速是还是需要0.04㎡取一个测试点吗

王宇晗 | 2024-11-13 06:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

阿龙 2024-11-13 11:51 00 [回复]举报

 a)小截面风口(风口面积小于0.3㎡),可采用5个测点,见图1。
    b)当风口面积大于0.3㎡时,对于矩形风口,见图2,按风口断面的大小划分成若干个面积相等的矩形,测点布置在图2中每个小矩形的中心,小矩形每边的长度为200mm左右;

王宇晗   回复: 阿龙2024-12-13 12:42

谢谢您的回复,这个规范我了解过 但是就像我上方问题中说的1㎡左右的风口是否还应该按照这个要求测试就不是很明确了

0    0 [回复]举报

阿龙   回复: 王宇晗2024-12-24 09:40

实际工作中其实也没必要太一板一眼了,按照规范意思就是要多测几个点然后计算平均值就行了。

0    0 [回复]举报

王宇晗   回复: 阿龙2024-12-30 13:09

这不是讨论方法吗 我也不可能说没问出来活也不干了

0    0 [回复]举报