关于喷头安装在排管及风管上方的探讨及在镂空吊顶上方安装喷头是否改下喷

问题1:现场实际施工过程中,往往会碰到标准直立型喷头安装在不足1.2m的成排管道,桥架及风管上方,这样做是否满足规范要求,若要适用规范考虑适用自喷设计规范7.2.1还是7.2,;个人理解自喷设计规范7.2.1 并不适用于这样的现场,7.2.1提到的障碍物是在喷头距顶板75~150mm时障碍物底部到顶板喷头影响洒水效果;而现场实际的这种情况是喷头安装在视作障碍物的不足1.2m成排管道,桥架及风管的上方,障碍物是不到顶的间断障碍物,故7.2.2更适用现场;

问题2:当直立型喷头安装在满足通透率的格栅吊顶上时喷头下方与格栅吊顶间存在视为障碍物的不大与1.2m的排管,桥架及风管,且喷头无法满足与障碍物的水平距离;此时(格栅吊顶内无可燃物)是否可将直立型喷头改成下垂型喷头,;求大师解答

叮当口袋 | 2025-04-16 23:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防资源网 2025-04-17 13:43 00 [回复]举报

如果喷头正好在风管上方,最好增设一个喷头在风管下

EHS专家-DL 2025-04-17 14:04 00 [回复]举报

问题1:喷头安装在不足1.2m的成排管道、桥架及风管上方是否合规?适用规范7.2.1还是7.2.2?

  1. 规范适用性分析

    • 喷头安装在障碍物(宽度<1.2m的管道、桥架、风管)‌上方‌,且障碍物属于不到顶的间断障碍物,此时应优先适用‌7.2.2条‌关于“间断障碍物”的规定,即喷头与障碍物的水平距离需满足喷洒覆盖要求,且无需因障碍物宽度不足1.2m而强制调整喷头位置‌。
  2. 施工合规性判断

    • 若喷头溅水盘与顶板距离符合75-150mm要求,且障碍物宽度未超过1.2m,则允许喷头直接安装在障碍物上方,但需确保障碍物下方无未被覆盖的保护区域‌。若障碍物导致喷头洒水被遮挡,则需按7.2.3条增设喷头或调整喷头位置‌。

问题2:格栅吊顶下方存在障碍物时,直立型喷头可否改为下垂型?

  1. 调整喷头类型的可行性

    • 当格栅吊顶通透率满足规范要求(通常≥70%),且吊顶内无可燃物时,允许将直立型喷头改为下垂型喷头,但需满足以下条件:
      • 下垂型喷头溅水盘应与格栅吊顶平齐,且与吊顶装饰盖板紧密贴合‌;喷头与下方障碍物的垂直距离应≥25mm,且障碍物宽度≤1.2m时,可不增设喷头‌。
  2. 障碍物影响的处理

    • 若障碍物(如排管、桥架)与喷头水平距离不足,导致下垂型喷头洒水被遮挡,则需按规范要求调整喷头位置或增设喷头,确保喷水覆盖范围无盲区‌。若改为下垂型喷头后仍无法满足覆盖要求,则需重新评估吊顶通透率或采用其他加强措施(如加密喷头)‌。

综合结论

  1. 问题1‌:障碍物宽度<1.2m时,优先适用7.2.2条,喷头可直接安装在障碍物上方,但需验证喷水覆盖效果‌
  2. 问题2‌:格栅吊顶通透率达标且无可燃物时,允许直立型改为下垂型喷头,但需确保溅水盘位置合规且无遮挡‌