消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防应急照明是否可以兼用日常照明

请教各位,商业建筑内的楼梯间消防应急照明是否可以兼作日常照明,目前设计了一套DC36V的消防应急照明,又设计了一套AC220V的普通照明,基于成本考虑想减少一套,问设计院回复说不可以,查了相关规范,住宅建筑采用自带蓄电池的灯具可以兼用日常照明,商业这块也没说?有没有知道的?

消防网友73006 | 2021-12-28 11:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

吴俊 2021-12-28 17:14 00 [回复]举报

应急照明可以用于平时照明的,需要购买具有两个单独回路及照明的灯具,里面需要有两组线,一个是普通用电的,还有一个是消防配电线路;消防配电线路不能受开关等控制

发条橙子   回复: 吴俊2023-10-11 10:41

有这种灯具吗


0    0 [回复]举报

阳光哥哥 2021-12-31 18:40 00 [回复]举报

4 设置在距地面8m及以下的灯具的电压等级及供电方式应符合下列规定:
      1)应选择A型灯具;
      2)地面上设置的标志灯应选择集中电源A型灯具;
      3)未设置消防控制室的住宅建筑,疏散走道、楼梯间等场所可选择自带电源B型灯具。

忙里偷闲 2022-02-11 11:10 10 [回复]举报

《消防应急照明和疏散指示系统技术标准》3.1.6 住宅建筑中,当灯具采用自带蓄电池供电方式时,消防应急照明可以兼用日常照明。商业建筑不可以。

关闭

关闭

手机APP下载