声光报警器的启动方式?

一个感烟探测器能触发声光报警器吗?

新颖 | 2022-03-24 11:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

石小东 2022-03-24 18:17 00 [回复]举报

如果在气体灭火系统里会

法亦有道 2022-03-24 22:16 00 [回复]举报

不能,根据《火灾自动报警系统设计规范》(GB50116-2013 第4.8.1 条 火灾自动报警系统应设置火灾声光警报器,并应在确认火灾后启动建筑内的所有火灾声光警报器。

肖冰 2022-03-24 23:55 00 [回复]举报

可以

林继青 2022-03-25 08:56 00 [回复]举报

不能,启动需要满足逻辑“与”的两个信号

充楞装傻 2022-03-25 10:17 00 [回复]举报

可以。

你不能低于规范,但可以超越规范。1点联动当然兼容了2点联动。

只要有需求,法律、规范没有禁止,就可以做

天天消防 2022-05-19 09:40 00 [回复]举报

联动公式怎么做都可以,别说一个烟感触发声光,一个消报启动消防泵。喷淋泵,启风机,切非消防电源都可以做到,一个烟感启动发射原子弹都能办到。就是规范不允许

消防小学生刘振 2022-06-07 17:56 00 [回复]举报

功能上当然可以实现,但新规范没有要求一点联动,而且也不建议一点触发声光报警器,因为误报情况时有发生,不能每次都触发声光报警器,引起不必要的恐慌,还是要在确定火灾后再触发声光报警器动作。

珍珠baby 2022-06-21 15:23 00 [回复]举报

你想设置成一点联动那是没问题的,都可以做到,问题是规范没有规定一点启动,而且声光一个烟感启动误报的可能性大,每次你都声光启动造成不必要的恐慌