疏散指示灯具是否可以安装在走道上部

如果建筑物有维护结构,比如办公楼的走廊有维护结构,要求是安装在墙面1米以下位置,如果方向标志灯具数量不足需要增加一部分,是否可以把方向标志灯具安装在天棚的中间或走道的上部靠近天棚处

水上漂123 | 2022-04-01 07:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

9527 2022-04-01 08:51 00 [回复]举报

不可以。

1、不符合人的视觉习惯。

2、上部容易被烟气遮挡。

3、可能导致不能保持视觉连续。

4、规范要求,有围护结构的应安装在墙面、柱等,1米以下位置。

充楞装傻 2022-04-08 11:15 00 [回复]举报

4.5.11 方向标志灯的安装应符合下列规定:
    1 应保证标志灯的箭头指示方向与疏散指示方案一致。
    2 安装在疏散走道、通道两侧的墙面或柱面上时,标志灯底边距地面的高度应小于1m。
    3 安装在疏散走道、通道上方时:
      1)室内高度不大于3.5m的场所,标志灯底边距地面的高度宜为2.2m~2.5m;
      2)室内高度大于3.5m的场所,特大型、大型、中型标志灯底边距地面高度不宜小于3m,且不宜大于6m。
    4 当安装在疏散走道、通道转角处的上方或两侧时,标志灯与转角处边墙的距离不应大于1m。
    5 当安全出口或疏散门在疏散走道侧边时,在疏散走道增设的方向标志灯应安装在疏散走道的顶部,且标志灯的标志面应与疏散方向垂直、箭头应指向安全出口或疏散门。
    6 当安装在疏散走道、通道的地面上时,应符合下列规定:
      1)标志灯应安装在疏散走道、通道的中心位置;
      2)标志灯的所有金属构件应采用耐腐蚀构件或做防腐处理,标志灯配电、通信线路的连接应采用密封胶密封;
      3)标志灯表面应与地面平行,高于地面距离不应大于3mm,标志灯边缘与地面垂直距离高度不应大于1mm。