消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下防烟楼梯间

地下防烟楼梯间采用自然排烟,前室在顶部设置加压风口,那么防烟楼梯间的开窗要满足什么要求?

建筑工 | 2022-04-08 23:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

刘丽波 2022-04-10 08:06 00 [回复]举报

如果防烟楼梯间不与地上共用,且为一层,执行烟规3.1.6条,直通室外的门或1.2平的窗;如与地上共用或超过一层,建议机械加压送风 。对于后者,20k607图示中给出开2平的窗,设计需咨询审图老师是否认可。


消防网友69339 2022-04-10 11:08 00 [回复]举报

最高点1平方米固定窗

十万嬉皮 2022-04-11 10:18 00 [回复]举报

2平方,楼梯间的自然排烟最顶部的1平方可开启外窗也可以算在2平方里面。

充楞装傻 2022-04-11 10:26 00 [回复]举报

防烟楼梯间里面不会有烟 为什么要排烟? 

3.3.11 设置机械加压送风系统的封闭楼梯间、防烟楼梯间,尚应在其顶部设置不小于1m2的固定窗。靠外墙的防烟楼梯间,尚应在其外墙上每5层内设置总面积不小于2m2的固定窗。

我认为仅在前室加压送风,也适用本条款(有加压送风系统).


G-A-O 2022-10-20 10:56 00 [回复]举报

地下防烟楼梯间与地上楼梯不合用,需满足有效开窗面积2平方,顶部开设的1平方外窗可计入面积总数。若为封闭楼梯间,仅在首层开1.2平方以上的外窗或者直通室外的门即可。

你的项目是地下防烟楼梯间,且需要看是地下几层,1~2层的话,不大于10m,可以采用自然,若地下3层,直接机械吧。

关闭

关闭

手机APP下载