消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

厂房与仓库之间在一层做连廊,对于建筑的防火要求

如下图,情况:厂房与仓库之间做一个连廊。连廊处于一层,四周无墙,只有顶。连廊结构与厂房和仓库是拖开,连廊下净空为5米,消防车可正常通行,地面标高同室外道路标高。

连廊对应处的厂房和仓库门需做防火门吗,墙体做彩钢板墙是否可以?

如果仓库做为敞开式的是否可以?

连廊下方直接是室外是室外安全区域吗?



静学者 | 2022-04-13 17:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

充楞装傻 2022-04-13 17:40 00 [回复]举报


双面彩钢夹岩棉80mm以上的墙~才算得上2级,2个2级丙类 防火间距10米。

满足防火间距又无可燃物的连廊~6.6.4 连接两座建筑物的天桥、连廊,应采取防止火灾在两座建筑间蔓延的措施。当仅供通行的天桥、连廊采用不燃材料,且建筑物通向天桥、连廊的出口符合安全出口的要求时,该出口可作为安全出口。

安全出口的门~满足防火间距~即使正对,也不用不装。。。

龙虾   回复: 充楞装傻2022-04-14 06:25

防火分区你怎么算面积

0    0 [回复]举报

静学者   回复: 龙虾2022-04-18 11:26

有关于防火分区面积,及建筑面积课题,对于雨棚下的室外空间,是算建筑面积,但可不计入防火分区面积内。

0    0 [回复]举报

乌伤浪人 2022-04-16 21:02 10 [回复]举报

看图纸截图,如果丙仓、丙厂的其他部位耐火等级满足二级以上要求,非承重外墙采用单层的彩钢板是不能满足二级耐火等级要求的,如果不能满足相应的耐火等级要求,防火间距都可能不足,因此不能采用单层彩钢板。如果厂房和仓库满足二级耐火等级要求,防火间距已符合规范要求,厂房、仓库的门都无需采用防火门。连廊下方属于室外安全区域。丙仓连廊处开口可不设置外门。

静学者   回复: 乌伤浪人2022-04-18 11:32

谢谢,你这给了,我一个新思路,只要满足二级耐火,防火间距又满足要求,敞开连廊下的门就是当普通外门来看,不用按图集上防火门来考虑了?

另外,建规3.2.12中除甲乙及高层仓库外,一、二级耐火等级建筑非承重外墙,不燃性墙体时,耐火极限不应低于0.25H .理解这一条是对于不太危险的工业用房,外墙耐火可适当降低标准了。


0    0 [回复]举报

乌伤浪人   回复: 静学者2022-04-18 14:43

如果单层彩钢板的耐火等级达到相应标准,就可以采用。

0    0 [回复]举报

关闭

关闭

手机APP下载