消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问避难层、避难间、避难走道,要设自喷喷头吗?

避难层是作为安全区域考虑的,跟楼梯间类似。实际工程中楼梯间内都不设喷头,那避难层里是否也可以不设?


建规5.5.23.6:"避难层应设置消火栓和消防软管卷盘。”我这样理解:消火栓本来就是整栋楼均要设的,这里单独又提出来要设。自喷也是整栋楼要设,这里却没有单独提出来要设。


是否说明避难层可以不设?

朦胧的朱迪 | 2022-09-07 10:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

林继青 2022-09-07 11:43 00 [回复]举报

消火栓提出要设卷盘,其他部位有可能设了消火栓不用设卷盘;再说在这一条款下没单独提出来,并不代表其它条款不需要遵守和执行

朦胧的朱迪   回复: 林继青2022-09-07 12:14

谢谢回复,有避难层的建筑都要设软管卷盘,这条应该不是为了突出软管卷盘才特意提的。我是考虑消火栓和喷淋同属于水系统,规范为啥只提消火栓,搞了个区别对待。

0    0 [回复]举报

林继青   回复: 朦胧的朱迪2022-09-07 14:10

规范可没有规定有避难层的建筑都要设卷盘哦,只规定避难层要设

0    0 [回复]举报

永锅 2022-09-15 17:15 10 [回复]举报

避难层里要设置喷头。


建筑高度大于100米的公共建筑应设置避难层,该建筑应为一类高层公共建筑;


建规8.3.3条明确规定一类高层公共建筑除游泳池、溜冰场外,其他地方都应设。



朦胧的朱迪   回复: 永锅2022-09-19 15:03

你好,感谢回复,只是讨论一下,按这个条文,楼梯间里也是要设喷头的,因为楼梯间也没被明确除外。但是工程实际里面楼梯间向来是不做喷头的。

0    0 [回复]举报

永锅   回复: 朦胧的朱迪2022-09-21 17:27

楼梯间内不得布置可燃物,包括装修材料顶、墙、地均应采用A级材料。

避难层可兼作设备层,设备层会布置易燃、可燃液体或气体管道,避难区与管道井布置在同一平面,虽说进行了防火分隔,但存在一定的火灾危险性。(建规5.5.23第4条)

基于以上两点,个人认为楼梯间内可不设置喷头,但避难层内要设置喷头。

0    0 [回复]举报

朦胧的朱迪   回复: 永锅2022-09-26 16:39

这个思路有一定道理

0    0 [回复]举报

关闭

关闭

手机APP下载