消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电室长度超过7m时,应设2个出口,并宜布置在配电室两端。当配电室双层布置时,楼上配电室的出口应至少设一个通向该层走廊或室外的安全出口.那么另外一个出口可以开向其他房间进行疏散吗

配电室长度超过7m时,应设2个出口,并宜布置在配电室两端。当配电室双层布置时,楼上配电室的出口应至少设一个通向该层走廊或室外的安全出口.那么另外一个出口可以开向其他房间进行疏散吗

正在学习中 | 2023-05-29 10:03
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-05-29 10:59 00 [回复]举报

建筑防火通用规范 GB55037-2022

术语:

12 安全出口 safety exit     供人员安全疏散用的楼梯间和室外楼梯的出入口或直通室内外安全区域的出口。

13 疏散门 evacuation door     设置在疏散出口上满足人员安全疏散要求的门。

14 疏散出口 exit     建筑中在火灾时供人员逃离着火区域或建筑的出口,包括安全出口和房间疏散门。


无论单层疏散、还是双层疏散,开向其他房间的门不是安全出口,也不是疏散出口或疏散门,不满足应设置两安全出口的要求,所以不可以


当然,如果满足建筑设计防火规范 GB50016-2014(2018年版)中的要求,可以设一个安全出口或疏散门

“5.5.5 除人员密集场所外,建筑面积不大于500m²、使用人数不超过30人且埋深不大于10m的地下或半地下建筑(室),当需要设置2个安全出口时,其中一个安全出口可利用直通室外的金属竖向梯。    

除歌舞娱乐放映游艺场所外,防火分区建筑面积不大于200m²的地下或半地下设备间、防火分区建筑面积不大于50m²且经常停留人数不超过15人的其他地下或半地下建筑(室),可设置1个安全出口或1部疏散楼梯。     除本规范另有规定外,建筑面积不大于200m²的地下或半地下设备间、建筑面积不大于50m²且经常停留人数不超过15人的其他地下或半地下房间,可设置1个疏散门。


正在学习中   回复: 安洪全2023-05-29 15:49

谢谢,确实通规明确说明了,不让借用

0    0 [回复]举报

安洪全   回复: 正在学习中2023-05-29 16:12

客气,互相学习,共同进步。

0    0 [回复]举报

关闭

关闭

手机APP下载