关于作用面积

麻烦问一下  作用面积这个概念怎么理解?比如说一栋建筑面积为20000平方米的高层办公楼,采用湿式自动喷水灭火系统,系统的作用面积是160平方米。这个要怎么理解

消防网友80587 | 2020-12-14 11:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2020-12-14 12:52 00 [回复]举报

喷规术语里有定义:

消防网友19680 2020-12-15 14:23 00 [回复]举报

作用面积是针对闭式系统而言的。简单理解,闭式系统是哪里着火哪里的喷头就会动作喷水,所谓的作用面积就是在规定面积(您说的160㎡)范围内喷头动作在该区域能够满足规范规定中的喷水强度,如果喷头动作的太多了,超过作用面积就无法保证每平方米喷水强度。您说的20000平方米理解为设置面积,160㎡理解为实际喷水的面积。