建筑防火通用规范 GB55037-2022》第6.4.7 下列部位的窗的耐火性能不应低于乙级防火窗的要求:
                                                                       1 歌舞娱乐放映游艺场所中房间开向走道的窗;
                                                                       2 设置在避难间或避难层中避难区对应外墙上的窗;
                                                                      3 其他要求耐火极限不低于2.00h的防火隔墙上的窗。

是否可以理解为:1、非 歌舞娱乐放映游艺场所中房间开向走道的窗可以为普通玻璃窗;2、其他要求耐火极限低于2.00h的防火隔墙上的窗可以为普通玻璃窗。3、房间开向走道的窗的开窗面积有没有限制?

月亮哥哥 | 2023-11-01 11:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

胡胡203 2023-11-01 16:08 00 [回复]举报

这个没有明确的规定可以参考各地方的规定:

石家庄市消防设计审查疑难问题操作指南(2021年版) 5.0.16 疏散走道两侧的隔墙能否设普通玻璃窗?     处理意见:一、二级耐火等级建筑的疏散走道两侧的隔墙的耐火极限为1.00h,疏散走道两侧窗的耐火完整性不应低于1.00h。

江苏省建设工程消防设计审查验收常见技术难点问题解答2.0   

1.3.4.2 民用建筑走道两侧设置的玻璃隔断、为了通风在疏散走道隔墙上设置的窗户等耐火极限是否有要求?     答:《建规》中对疏散走道两侧门窗的耐火极限没有明确规定。当疏散走道两侧采用玻璃隔断或窗户时(包括全部和局部),玻璃隔断或窗户(包括同一墙面上的普通门的面积)的面积对应走道房间墙面投影面积大于50%时,应满足耐火极限1.0h的要求。    《建规》第2.1.10条关于耐火极限的名词解释中已经明确,此时间为从受到火的作用起,至失去承载能力、完整性或隔热性时止,三种情况均应包括。