消防泵、喷淋泵自动启泵,远程停泵问题

【消防给水及消火栓系统技术规范 GB50974-2014】   11.0.2 消防水泵不应设置自动停泵的控制功能,停泵应由具有管理权限的工作人员根据火灾扑救情况确定。

规范只要求不应自动停泵,为什么现场遇到的情况,自动启泵,也不能远程停泵。

南明离火 | 2024-01-12 10:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

安洪全 2024-01-15 08:58 00 [回复]举报

如果有自动停泵的设置,万一救火时凑巧触发了停泵,会延误造成火灾的蔓延

相比火灾的危害,无论水渍损失或水的浪费都显得没有那么重要了(而且一般都会回收水的措施)

南明离火   回复: 安洪全2024-01-16 09:19


可能我没描述准确,意思是水泵自动启泵了,可否消控室多线盘远程停泵?

0    0 [回复]举报

安洪全   回复: 南明离火2024-01-17 08:48

多线远程可以停泵

0    0 [回复]举报

陈晓茂   回复: 安洪全2024-01-20 05:37

自动启泵的情形,远程多线应该不能停泵。只能是自动启泵信号消失或水泵控制柜转到手动状态才能停泵。

1    0 [回复]举报

南明离火   回复: 陈晓茂2024-01-20 16:00

对,现场就是碰到这个问题,施工班组说 自动启,远程停不了

这个技术上能否做到,自动启泵情况下,远程停

0    0 [回复]举报

牛疼   回复: 南明离火2024-01-22 13:47

技术上能做到,但是如果有此功能,就有误操作或异常情况的可能出现,而导致需要用水的时候无水可用。

0    0 [回复]举报

2024-01-22 12:00 20 [回复]举报

弄清楚原理:自动起泵依靠压力开关的24v(此电源由水泵控制柜提供)回路闭合起泵,只要压力开关回路不断开泵就不会自动停止;多线启动是另外的24v(此电源由消防主机提供)回路,自动起泵后按多线停止按钮应无法停泵。

南明离火   回复: 2024-01-24 09:51

好像确实如此

0    0 [回复]举报