试验消火栓是否需设置消火栓报警按钮

屋顶的试验消火栓是否需设置消火栓报警按钮,有的设计有有的设计没有

消防网友65069 | 2024-01-14 15:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

阳明心 2024-01-15 11:13 00 [回复]举报

如果大楼本身有火灾自动报警系统的,应设消火栓报警按钮。

yizhongdayang 2024-01-16 08:30 10 [回复]举报

试验消火栓设置的目的是为了检查消火栓系统的运行状况以及测试消火栓系统的功能。由于消火栓泵由低压压力开关或流量开关连锁控制启动,这就大大降低了试验消火栓设置消火栓按钮的必要性,毕竟用试验消火栓测试消火栓系统功能时,也不要需用消火栓按钮启泵,低压压力开关或流量开关就可以满足要求。

国家建筑标准设计图集《室内消火栓安装》(15S202)P54页,说明的第2条:消防按钮是否设置由设计确定。如下图所示:

可见,试验消火栓未要求必须设置消火栓按钮,是否要设置,还是应由设计单位的设计人根据项目具体情况确定。