消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

压力表数值不一样


消火栓系统设置了稳压灌稳压,发现稳压泵管路上压力表和系统出水管上压力表的压力值不一样,压力表均设于水泵房内,都是启泵用的电接点压力表,但泵在未启动的时候两压力表数值不一至,这是正常的吗?如果不正常,原因是什么?如何解决这种问题?

柠檬不萌 | 2024-03-18 08:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

牛疼 2024-03-19 13:18 00 [回复]举报

要么是表坏了,要么是中间有减压阀。

柠檬不萌   回复: 牛疼2024-03-20 16:33

没有减压阀

0    0 [回复]举报

牛疼   回复: 柠檬不萌2024-03-25 09:48

稳压罐的作用不是稳系统水压的;

稳压泵、稳压罐、应急泵,应该是一共至少3个压力表;

稳压泵与应急泵通厂应该是一个在顶部一个在底部,如果是老旧项目,可能稳压泵与应急泵在同一水泵房内;

应急泵出口有个止回阀,压力表安装在阀前或者阀后的位置不同,压力也是不一样的;

目前为止,对于所说的问题叙述不太清楚,可以简单画个示意图看看。


0    0 [回复]举报

简@风格 2024-03-19 13:42 00 [回复]举报

最好请补充一下:示意图  没明白你这个问题的描述

柠檬不萌   回复: 简@风格2024-03-20 16:36

就是消火栓系统出水总管上的压力表压力值和稳压泵出水管上的压力值有小点差距,在泵都未启动的时候

0    0 [回复]举报

消防网友70233 2024-03-22 11:02 00 [回复]举报

两个表有高差吧?表显不一样正常呀

wzn128 2024-04-08 19:22 00 [回复]举报

看两个压力表的压力值相差多少,按理说有采用相同的厂家同一批次的压力表压力值显示应一样或有0.10MPa左右的误差。你可以通过拆一个压力表装到另一个压力表位置上确认你的问题的原因是什么引起的来判断。

关闭

关闭

手机APP下载