消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

宾馆达到自然排烟条件有哪些?

宾馆中间区域,共6间无窗房间,单个房间不满足50平方米,但无窗房间总面积大于200平方米,在无窗房间走道两头的近端开通了自然排烟,请问是否符合要求,根据哪条规范?是否需要按照规范强制在走道增加机械排烟?

鱼在水中游 | 2024-06-19 15:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

黄-江西省景德镇市 2024-06-19 15:45 10 [回复]举报

建议附图,需要综合性,不能只从一两个维度去判断,比如吊顶下净高、防烟分区最大长边、走道宽度等等。

@mad 2024-06-19 15:47 10 [回复]举报

可以自然排烟。

潘天坤 2024-06-19 15:51 10 [回复]举报

走道长度多少米,宽度多少米,走道有怎么样的排烟设施,是否两侧各有2平米的可开启外窗并且满足两侧自然排烟窗(口)的距离不应小于走道长度的2/3?


根据建筑防烟排烟系统技术标准 GB51251-2017 第4.6.3条第3款规定:

当公共建筑仅需在走道或回廊设置排烟时,其机械排烟量不应小于13000m³/h,或在走道两端(侧)均设置面积不小于2㎡的自然排烟窗(口)且两侧自然排烟窗(口)的距离不应小于走道长度的2/3。


建筑防火通用规范实施指南有提到:在建筑中存在无窗房间的区域,当每间房间的建筑面积小于或等于50平方米, 这些房间的总建筑面积大于200平方米时(这条规定的总建筑面积不包括房间外的疏散走道等公共区域的面积),在房间内可以不设置排烟设施,但应在房间外的公共区设置排烟设施。

安洪全 2024-06-19 16:44 20 [回复]举报

建筑防火通用规范 GB55037-2022

8.2.5说的是需要设排烟设施,没说强制机械排烟,如果走道两端的自然排烟口满足排烟需求的话,不需要强制上机械排烟。

关闭

关闭

手机APP下载