消火栓箱的设置条件

消火栓箱的设置范围?哪些条件不用设置消火栓箱

哇咔 | 2024-06-24 09:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

香.香 2024-06-24 12:04 00 [回复]举报

室外消火栓不需要设置消火栓箱,设置干式消防竖管的不需要设置消火栓箱

潘天坤 2024-06-24 12:04 00 [回复]举报

可以结合建筑防火通用规范和建规要求综合考虑

建筑防火通用规范 GB55037-2022第8.1.7条规定:

除不适合用水保护或灭火的场所、远离城镇且无人值守的独立建筑、散装粮食仓库、金库可不设置室内消火栓系统外,下列建筑应设置室内消火栓系统:
    1 建筑占地面积大于300㎡的甲、乙、丙类厂房;
    2 建筑占地面积大于300㎡的甲、乙、丙类仓库;
    3 高层公共建筑,建筑高度大于21m的住宅建筑;
    4 特等和甲等剧场,座位数大于800个的乙等剧场,座位数大于800个的电影院,座位数大于1200个的礼堂,座位数大于1200个的体育馆等建筑;
    5 建筑体积大于5000m³的下列单、多层建筑:车站、码头、机场的候车(船、机)建筑,展览、商店、旅馆和医疗建筑,老年人照料设施,档案馆,图书馆;
    6 建筑高度大于15m或建筑体积大于10000m³的办公建筑、教学建筑及其他单、多层民用建筑;
    7 建筑面积大于300㎡的汽车库和修车库;
    8 建筑面积大于300㎡且平时使用的人民防空工程;
    9 地铁工程中的地下区间、控制中心、车站及长度大于30m的人行通道,车辆基地内建筑面积大于300㎡的建筑;
    10 通行机动车的一、二、三类城市交通隧道。


建筑设计防火规范 GB50016-2014(2018年版)8.2.2条规定:

本规范第8.2.1条未规定的建筑或场所和符合本规范第8.2.1条规定的下列建筑或场所,可不设置室内消火栓系统,但宜设置消防软管卷盘或轻便消防水龙:
    1 耐火等级为一、二级且可燃物较少的单、多层丁、戊类厂房(仓库)。
    2 耐火等级为三、四级且建筑体积不大于3000m³的丁类厂房;耐火等级为三、四级且建筑体积不大于5000m³的戊类厂房(仓库)。
    3 粮食仓库、金库、远离城镇且无人值班的独立建筑。
    4 存有与水接触能引起燃烧爆炸的物品的建筑。
    5 室内无生产、生活给水管道,室外消防用水取自储水池且建筑体积不大于5000m³的其他建筑。

安洪全 2024-06-24 14:01 10 [回复]举报

个人理解:

只要需要配水带的,就应该设消火栓箱。


简单粗暴的理解,除了埋地式的室外消火栓,和住宅只配干式消防竖管的,其余系统都应该设箱子

最帅游客 2024-06-25 10:39 00 [回复]举报

一般说的室内消火栓默认的是带箱子的。除明文规定可以设置不带消火栓箱的消火栓(比如建筑8.2.1)