请问乙类(厂房)与其他建构筑是否能够贴临

注2最后一款规定了不应与乙类厂房办公室、休息室规定外的其他建筑贴临,但是第一款又规定使用防火墙可以不限防火间距  怎么理解这里呢 

uprui0 | 2024-06-24 21:19
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

香.香 2024-06-25 09:44 20 [回复]举报

335是指厂房内管理生产、调度等的办公用房和供人员休息的临时用房,这些用房是不可能脱离厂房的,对于甲乙类厂房它可以贴临但要符合规范要求,对于丙类它可以直接设置在厂房内且同时符合设置要求。你勾画的蓝色字体其它建筑(除办公室、休息室外)是不能于甲乙厂房、仓库贴临的,它是指这个意思。你不能理解的那个点(一定条件下采用防火墙时防火距离不限)。它指的是两栋独立的建筑。有个问题 你要清楚一下,贴临是指两个物体之间只有一面墙挨着,而防火间距是两个不同的建筑,他们是独立存在的,没有合用的任何墙体,哪怕是不限防火间距他们两者也是各自有各自的防火墙,而贴临就不一样哦。

phone0224 2024-06-25 10:07 00 [回复]举报

个人认为:注2的前面一款,说的是两个厂房之间的间距问题,第二款说的是与其他民用建筑之间的间距问题。您说的其他建构筑物如果是厂房就可以按第一款来界定,如果是民用就得按第二款界定。

消防网友68723 2024-06-25 10:57 00 [回复]举报

1、甲甲4M

2、甲、乙不贴3.3.5中规定外的

3、除此其它不限

最帅游客 2024-06-25 11:07 00 [回复]举报

仅辅助用房可以贴临,且其耐火等级,防火分隔及安全出口等须符合要求。